首页 PLC论坛 西门子SIEMENS
主题:我需要帮助啊
点击:961 回复:2
To: shimon901@hotmail.com
Subject: Number shaft I
Date: Tue, 06 Feb 2007 07:10:51 +0000
>Dear sir.!!
>We have a problem about signalling system,
>Signal PLC was suddenly stopped often(1 or 2 times in 8 hours)
>period).
>But this problem resolved manual restart(energy off then on),
>warm restart on PLC program(simatic s7) or
>manual start on PLC Module.
>There is a error log at the bottom.
>Thank you
>Best regards,
>Halim
>Diagnostic buffer of module CPU 313C-2 DP
>Order No./ Description Component
> Version
>6ES7 313-6CE01-0AB0 Hardware 1
>- - - Firmware V
>2.0.10
>Rack: 0
>Slot: 2
>Event 1 of 10: Event ID 16# 4302
>Mode transition from STARTUP to RUN
>Startup information:
>- Time for time stamp at the last backed up power on
>- Single processor operation
>Current/last startup type:
>- Automatic warm restart after backed up power on
>Permissibility of certain startup types:
>- Manual warm restart permitted
>- Automatic warm restart permitted
>Last valid operation or setting of automatic startup type at power
>on:
>Previous operating mode: STARTUP (warm restart)
>Requested operating mode: RUN
>Incoming event
>09:17:16.291 AM 02/05/2007
>Event 2 of 10: Event ID 16# 1382
>Request for automatic warm restart
>STOP due to: STOP caused by stop switch being activated
>- Startup without modified system configuration
>- No difference between setpoint and actual configuration
>Last valid operation or setting of the automatic startup type at
>power on:
>Requested OB: Startup OB (OB100)
>Priority class: 27
>Incoming event
>09:17:16.290 AM 02/05/2007
>Event 3 of 10: Event ID 16# 4301
>Mode transition from STOP to STARTUP
>power on:
>Previous operating mode: STOP (internal)
>Requested operating mode: STARTUP (warm restart)
>Incoming event
>09:17:15.593 AM 02/05/2007
>Event 4 of 10: Event ID 16# 38C4
>Distributed I/Os: station return
>Address of the affected DP slave: station number: 6
>DP master system ID: 1
>Log. base address of the DP slave: Input address: 1019
>Log. base address of the DP master: 32767
>Requested OB: Rack failure OB (OB86)
>OB not found, or disabled, or cannot be started in the current
>operating mode
>External error, Outgoing event
>09:17:15.216 AM 02/05/2007
>Event 5 of 10: Event ID 16# 38C4
>Address of the affected DP slave: station number: 5
>Log. base address of the DP slave: Input address: 1020
>operating mode
>09:17:15.126 AM 02/05/2007
>Event 6 of 10: Event ID 16# 38C4
>Address of the affected DP slave: station number: 4
>Log. base address of the DP slave: Input address: 1021
>operating mode
>09:17:15.036 AM 02/05/2007
>Event 7 of 10: Event ID 16# 38C4
>Address of the affected DP slave: station number: 3
>Log. base address of the DP slave: Input address: 1022
>operating mode
>09:17:14.944 AM 02/05/2007
>Event 8 of 10: Event ID 16# 3842
>Module OK
>Module type: Distributed I/0s
>Input address: 1019
>User information available
>Diagnostic interrupt from substitute
>Requested OB: Diagnostic interrupt OB (OB82)
>operating mode
>09:17:14.878 AM 02/05/2007
>Event 9 of 10: Event ID 16# 3842
>Module OK
>Input address: 1020
>operating mode
>09:17:14.876 AM 02/05/2007
>Event 10 of 10: Event ID 16# 3842
>Module OK
>Input address: 1021
>operating mode
>09:17:14.873 AM 02/05/2007
>_________________________________________________________________
>Real-time chat with your friends - Free download - MSN Messenger
>http://messenger.msn.com/?mkt=tr
这是我们一个客户发过来的,谁帮忙翻译下,谢谢~
07-02-08 14:23
这些英文还看不懂可真要好好学一下了!
07-02-08 15:49
楼上的朋友:
你的S7-300故障应当是, 从站3,4,5,6无法与CPU313通讯. 请在你的S7程序中, 加入OB86 (分布式机架或DP从站故障). 当然, OB121, OB122都要加到程序里.
如果你的硬件有诊断功能, 也可以加 OB82.
添加上述的OB块之后, CPU工作时遇到从站硬件故障, 都不会停机!
07-02-08 17:33
